?- Making a RV to Generator Power Cord 30 amp

I'm making a cord from my generator to a rv.

On my generator, I have a L14-30 amp 120/240 twist lock receptable.

Do I just use one hot side to make a RV extension cord?

Or can you tie two hots together?

Does it hurt the generator to run on 1 hot side?

(it seems to sound different when a load is on one hot side, i've been told to equalize the load across both hots if possible)

Thanks
Reply
Old Oct 25, 2007 | 07:26 PM
  #2  
Mechanos's Avatar
Registered User
 
Joined: Jan 2004
Posts: 843
Likes: 1
From: Kansas City, MO
No, you cannot simply tie both hot together.... unless you want the let the magic smoke out of your gen set. If you want 120V, then you will have to settle for running it off of one leg or the other.

Also, keep in mind that if the gen set is capable of producing 40A at 120V (for example), that is 40A combined.... 20A from one leg, 20A from the other. If you try to pull a 30A load from just one of the 20A legs, it will trip the circuit breaker.
Reply
Old Oct 25, 2007 | 07:49 PM
  #3  
jlipskoc's Avatar
Thread Starter
Registered User
 
Joined: Jun 2003
Posts: 396
Likes: 0
I can pull 30 amps from both legs, its a 7200 watt gen.

I've seen some generators with a single L5-30? 3 prong 120v plug that had both hots wired somehow, I'm guessing thru a series setup.

I know, sounds like a stupid question, but never hurts to ask

At the same time, I want to extend the generator life, so both sides are equal that would be cool, but doesn't sound like its feasible.
Reply
Old Oct 25, 2007 | 08:53 PM
  #4  
Fueling around's Avatar
Registered User
 
Joined: Mar 2003
Posts: 1,629
Likes: 0
From: Northwest, Minnesota USA
You cannot put both "hots" together to combine amperage. It is called a dead short.

It really depends on your generator if you can use one side of the voltage.
What brand and model do you have?

I have a Generac 5KW (7.2KW surge) generator which means 120/240V @ 20 amps. One of the 3 plugs on the panel is a 120V @ 30 amp twist lock. It draws power from 1 winding (hot) on the generator. This is common by using a 7KW generator for the extra wiring capacity. The generator must be rated for this usage.
Reply
Old Oct 25, 2007 | 08:55 PM
  #5  
XLR8R's Avatar
Registered User
 
Joined: Nov 2005
Posts: 7,785
Likes: 3
From: Pattonville, Texas
Don't connect those two 120Vac out-of-phase 30A circuits together w/o a load in between...

Don't allow any expensive Smoke to escape the genset!
Reply
Old Oct 26, 2007 | 07:01 AM
  #6  
jlipskoc's Avatar
Thread Starter
Registered User
 
Joined: Jun 2003
Posts: 396
Likes: 0
Actually its a PTO generator, similiar to this one. Run it off the tractor.

The guys ad was misleading, its a 11kw head, but turns out its a 7.2 kw head.
Only came with one 30 amp 120v twistlock, l5-30 or l6-30?, and duplex 120v 15 amp.

http://cgi.ebay.com/New-11kw-Generat...QQcmdZViewItem

They had it wired somehow in series, so it loaded both sides equally. I got the paper work from the factory, and rewired it, so I could get a full 60 amps from it. There is two hot and two neutral 10 gauge wires coming from the windings.

It works great now since I rewired it with a L14-30 twistlock. Got a transfer switch on the house now. I had to weld a frame for it, and buy a pto shaft, been a fun project overall. Used it alot around the house, and out in the field already.

It basically looks like this when its all done:
http://www.northerntool.com/webapp/w...8467_200308467
Reply
Old Oct 28, 2007 | 04:36 AM
  #7  
Jim Lane's Avatar
Administrator
20 Year Member
Liked
 
Joined: Nov 2004
Posts: 4,084
Likes: 235
From: Southern California
I am also on this Generator forum; there is a lot of valuable knowledge here.
http://www.smokstak.com/forum/forumdisplay.php?f=6
Jim
Reply
Old Oct 28, 2007 | 07:03 PM
  #8  
WestTN's Avatar
Registered User
 
Joined: Feb 2004
Posts: 415
Likes: 3
From: Sharon, TN & Okeechobee, FL
Get an electrician to help you with this. You definitly cannot wire the 2 120v windings in series. They are 180 degrees out of phase. 20 amps from each winding will give you either 2 120 volt 20 amp cicuits or 1 240volt 20 amp circuit. Those are the only possibilities from this generator.
Reply
Related Topics
Thread
Thread Starter
Forum
Replies
Last Post
DieselDaze
General Diesel Discussion
34
Nov 25, 2013 12:58 PM
Don T
General Diesel Discussion
8
Aug 1, 2011 08:47 PM
04ctd
Towing and Hauling / RV
1
Apr 23, 2010 10:07 AM
Math_Teacher
3rd Gen High Performance and Accessories (5.9L Only)
1
Feb 26, 2005 10:50 AM
CaptainDD
Performance and Accessories 2nd gen only
0
Nov 12, 2002 08:52 PM


Thread Tools
Search this Thread

All times are GMT -5. The time now is 12:58 PM.