Who makes the best Residential Generator
Ok Yall
Dad is looking to invest in a residential generator. Wants one that runs on propane. Cost is not a big factor. Reliability and longevity are the primary concerns. Its gonna get an auto disconnect. Dad wants one that will fire up everytime with no issues, for years to come. Looking for one in the 30-35 KW range.
Im thinking Cummins/Onan would be a nice unit, Im not a Generac fan. Im also not that savvy on such issues.
Enlighten me!
Thank in advance.
Dad is looking to invest in a residential generator. Wants one that runs on propane. Cost is not a big factor. Reliability and longevity are the primary concerns. Its gonna get an auto disconnect. Dad wants one that will fire up everytime with no issues, for years to come. Looking for one in the 30-35 KW range.
Im thinking Cummins/Onan would be a nice unit, Im not a Generac fan. Im also not that savvy on such issues.
Enlighten me!
Thank in advance.
#2
Registered User
Join Date: Jan 2008
Location: Houston
Posts: 1,719
Likes: 0
Received 0 Likes
on
0 Posts
I don't know alot of them, but I have heard some guys talking about how Generac are junk. Are you sure he wants a propane and not a inline natural gas? The natural gas ones are nice because in the event your electricity goes out, you don't have to go outside and mess with swapping out bottles.
They do cost alot more then the wheel around propanes though.
They do cost alot more then the wheel around propanes though.
#3
Administrator / Severe Concussion Aficionado
Thread Starter
Where we are there is no natural gas lines. (BOONDOCKS!!!! )
We have already contacted the local propane company from where we get our propane and will be procuring a 1000 gallon propane tank to furnish it. We are checking into local regs, but so far, have not found any issues with burying the propane tank. The propane company also has no issues with burying it either.
We have already contacted the local propane company from where we get our propane and will be procuring a 1000 gallon propane tank to furnish it. We are checking into local regs, but so far, have not found any issues with burying the propane tank. The propane company also has no issues with burying it either.
#4
Administrator / Scooter Bum
I have a Generac 15K connected to an automatic transfer switch and feed by a 500 gal in-ground propane tank.
It's wired to provide power to some lights, appliances, and outlets. (Not the HVAC though)
It 'excercises' itself by starting and running for 1/2 hour once a week.
It might be a little noisier than some other brands, but I placed mine behind the garage at the other end of the house.
It has worked flawlessly every time we have lost power so far.
It was included in the cost of "Casa Del Shovelhead" so I'm not sure how much it cost or the installation charges.
It's wired to provide power to some lights, appliances, and outlets. (Not the HVAC though)
It 'excercises' itself by starting and running for 1/2 hour once a week.
It might be a little noisier than some other brands, but I placed mine behind the garage at the other end of the house.
It has worked flawlessly every time we have lost power so far.
It was included in the cost of "Casa Del Shovelhead" so I'm not sure how much it cost or the installation charges.
#5
1st Generation Admin
I have no 1st-hand experience with a propane genset. That being said, while researching a genset for myself, it became clear to me that most genset makers derate a given genset when fueled with propane/natural gas (unless of course, it is built specifically to be fueled with propane).
Just be aware.
Just be aware.
#6
Administrator / Severe Concussion Aficionado
Thread Starter
I have no 1st-hand experience with a propane genset. That being said, while researching a genset for myself, it became clear to me that most genset makers derate a given genset when fueled with propane/natural gas (unless of course, it is built specifically to be fueled with propane).
Just be aware.
Just be aware.
Dad likes Kohler, looking into those too, anyone have anything to say about them, good bad or indifferent.
#7
Administrator / Severe Concussion Aficionado
Thread Starter
I have a Generac 15K connected to an automatic transfer switch and feed by a 500 gal in-ground propane tank.
It's wired to provide power to some lights, appliances, and outlets. (Not the HVAC though)
It 'excercises' itself by starting and running for 1/2 hour once a week.
It might be a little noisier than some other brands, but I placed mine behind the garage at the other end of the house.
It has worked flawlessly every time we have lost power so far.
It was included in the cost of "Casa Del Shovelhead" so I'm not sure how much it cost or the installation charges.
It's wired to provide power to some lights, appliances, and outlets. (Not the HVAC though)
It 'excercises' itself by starting and running for 1/2 hour once a week.
It might be a little noisier than some other brands, but I placed mine behind the garage at the other end of the house.
It has worked flawlessly every time we have lost power so far.
It was included in the cost of "Casa Del Shovelhead" so I'm not sure how much it cost or the installation charges.
Dad wants to be able to run EVERYTHING at any given time. No more misery during hurricane season.
Next door neighbor is a licensed electrician and will do all the install. He said a 25 KW should be sufficient to run everything all day long. Knowing Dad, he will buy a 40KW just to make sure.
Trending Topics
#8
Administrator / Scooter Bum
Sounds like he's on the right track.
I wasn't worried about powering the whole-house HVAC as I can power a room sized heater or AC in a pinch off an outlet.
I wasn't worried about powering the whole-house HVAC as I can power a room sized heater or AC in a pinch off an outlet.
#9
Proprietor of Fiver's Inn and Hospitality Center
I have looked at the Onan 25K unit - - it is sweet. And Onan has a great reputation for durability. Using this for emergency
service, surely he does not need 40KW. That is the same as a 150a service. Unless his house is very large, a 25K unit will give
the same as about a 100a service. In an emergency, no reason most houses could not exist on 100a for a few days. In fact,
I also looked at a 15K unit thinking of it for our home. Running the numbers, I figured it would be plenty for holding us for an
emergency for a few days. I have hooked up to my 6500w Onan from my fiver in an emergency and had lights, the bedroom AC unit,
refrigerator and freezer with no problem.
Bob
service, surely he does not need 40KW. That is the same as a 150a service. Unless his house is very large, a 25K unit will give
the same as about a 100a service. In an emergency, no reason most houses could not exist on 100a for a few days. In fact,
I also looked at a 15K unit thinking of it for our home. Running the numbers, I figured it would be plenty for holding us for an
emergency for a few days. I have hooked up to my 6500w Onan from my fiver in an emergency and had lights, the bedroom AC unit,
refrigerator and freezer with no problem.
Bob
#10
1st Generation Admin
30-35 KW. Is that a surge KW figure or constant KW figure?
My mess is a 25KW max constant with a 50KW surge capability (4-pole, low speed). As such, the 25KW comes out to be right at 110amps @ 240vac. Surge is twice as much. In my application (total electric home w/3-ton 16SEER heatpump), it's more than enough to start the largest motor load while everything else is on. The key there is the surge capacity (negligible light dimming and beating on the frig/freezer compressors).
Try to lean toward a 4-pole generator if at all possible (1500RPM slow speed) in terms of longevity. You'll fine many are in fact 2-pole (3500RPM high speed). It appears to me that the larger, 4-pole gensets offer by default a substantially larger surge figure due to the 4-pole windings.
Further, it takes approximately 45HP to come up with 25KW. Consider the economy of the more realistic light (as in low demand) genset operation ($). It costs to idle that big fella.
My mess is a 25KW max constant with a 50KW surge capability (4-pole, low speed). As such, the 25KW comes out to be right at 110amps @ 240vac. Surge is twice as much. In my application (total electric home w/3-ton 16SEER heatpump), it's more than enough to start the largest motor load while everything else is on. The key there is the surge capacity (negligible light dimming and beating on the frig/freezer compressors).
Try to lean toward a 4-pole generator if at all possible (1500RPM slow speed) in terms of longevity. You'll fine many are in fact 2-pole (3500RPM high speed). It appears to me that the larger, 4-pole gensets offer by default a substantially larger surge figure due to the 4-pole windings.
Further, it takes approximately 45HP to come up with 25KW. Consider the economy of the more realistic light (as in low demand) genset operation ($). It costs to idle that big fella.
#11
Administrator / Severe Concussion Aficionado
Thread Starter
It looks like the Kohler he fancies is a 27KW constant with a 38 kw surge. It is a 2 pole.
I like the Cummins/Onan that is rate at 30KW, it doesnt list a surge. It listed as a 2 pole also.
I like the Cummins/Onan that is rate at 30KW, it doesnt list a surge. It listed as a 2 pole also.
#12
Administrator
This is what your dad needs;
#13
Registered User
Join Date: Jan 2006
Location: hou. TX
Posts: 300
Likes: 0
Received 0 Likes
on
0 Posts
been shopping on govliquidation for a good 30-60kw mobile low rpm diesel unit... not the same as yours i imagine but i like something i can take with me incase the EDIT
Last edited by BC847; 07-05-2010 at 06:01 PM. Reason: Language
#14
Administrator / Severe Concussion Aficionado
Thread Starter
I agree that a portable diesel genset would be nice, but never will we leave the piece of earth that the generator is on. And yes I say we, cause if it gets that bad, thats were I will end up.
Dad has found a real nice Kohler unit, 35KW (constant), GM I-4 LP engine. Looking at that one. Might be a while before it goes in, might catch a wild hair and order one tomorrow, with him you never know.
Dad has found a real nice Kohler unit, 35KW (constant), GM I-4 LP engine. Looking at that one. Might be a while before it goes in, might catch a wild hair and order one tomorrow, with him you never know.
#15
Registered User
Join Date: Jan 2006
Location: hou. TX
Posts: 300
Likes: 0
Received 0 Likes
on
0 Posts
no doubt there are some nice stationary units too, all milsurp and diesels.
ima pick up something like this soon: http://www.govliquidation.com/auctio...&convertTo=USD
heres a 60kw stationary version:
http://www.govliquidation.com/auctio...&convertTo=USD
sorry im not knowledgeable about the propane units, but ive worked on plenty of diesel mep002a's
ima pick up something like this soon: http://www.govliquidation.com/auctio...&convertTo=USD
heres a 60kw stationary version:
http://www.govliquidation.com/auctio...&convertTo=USD
sorry im not knowledgeable about the propane units, but ive worked on plenty of diesel mep002a's