Assistance wiring a compressor, please

I'm in the process of setting up my new to me used high pressure compressor. I need some help with the electrical. It has a 5hp 230 volt Single Phase 23-24amp Baldor motor. I have the basic understanding that I need a Motor relay and a contactor, but I'm not sure what.

The compressor has a high pressure shut off switch and a high temp shut off switch, both of which should be rated at 240 volts.

On the compressor is a start button, and a selector switch for Off, Auto, or Manual.

So I guess I would take the 2 hot leads from my service panel to the relay, take the lead from the switches to the relay, then from the relay to the motor?

Any assistance would be appreciated.

Compressor photos are at: http://www.sdscuba.com/compressor
Old 10-11-2004, 01:53 PM
  #2  
Registered User
 
Haulin_in_Dixie's Avatar
 
Join Date: Nov 2001
Location: Branchville, Alabama
Posts: 4,199
Likes: 0
Received 1 Like on 1 Post
You will use a three wire cable. The two power wires go the the mains panel and to the main relay contacts. The third wire is grounded to the compressor and the power box at the house.

Generally the pressure switch is normally on and also the overheat switch. They would have to be in series going to the coil of the relay, or is the pressure switch part of the relay? Don't know, not enough information.
Old 10-11-2004, 03:16 PM
  #3  
Chapter President
 
Mostwanted's Avatar
 
Join Date: Feb 2003
Location: Independence, MO
Posts: 202
Likes: 0
Received 0 Likes on 0 Posts
without being there to look it all over, it will be hard to help.

First, is it 230V 3phase or single phase? If 3phase it must have 3phase 230volt supply or the motor will burn up. They do make single to 3phase converters tho.

Second you will need to make sure you get the corrct size motor starter for this motor (NEMA rating). The starter should have some auxillary contacts for your sealing circuit.

Post all of the data off of the motor and I will look it up and we will go from there. PRIAMRILY the catolog number.
Old 10-12-2004, 03:13 PM
  #4  
Registered User
Thread Starter
 
sdscuba's Avatar
 
Join Date: Aug 2002
Location: San Diego, CA
Posts: 81
Likes: 0
Received 2 Likes on 1 Post
Yes, the switches would be wired in series, they are all 240v low amp switches.


Motor Spec:

Catalog Number: JPL1409T
Specification Number: 36E774-190
Horsepower: 5
Voltage: 230
Hertz: 60
Phase: 1
Full Load Amps: 23
Usable at 208 Volts: 24
RPM: 3450
Frame Size: 184JP
Service Factor: 1.15
Rating: 40C AMB-CONT
Locked Rotor Code: F
NEMA Design Code: L
Insulation Class: F
Full Load Efficiency: 75
Power Factor: 88
Enclosure: OPEN
Baldor Type: 3634L
DE Bearing: 6207
ODE Bearing: 6205
Electrical Specification Number: 36WG0190
Mechanical Specification Number: 36E774
Base: RG
Mounting: F1
Old 10-12-2004, 03:39 PM
  #5  
Registered User
 
Haulin_in_Dixie's Avatar
 
Join Date: Nov 2001
Location: Branchville, Alabama
Posts: 4,199
Likes: 0
Received 1 Like on 1 Post
Ok so you will hook up the L1 and L2 as above discribed, the two wires to the relay contacts and the bare or third wire to ground and to the ground buss bar in the house box.

The relay normally called a motor starter generally has three contacts, for single phase you will only use two of them. These relays also generally have contacts for either normally on and normally off. Be sure to hook up as normally off.

The coil that operates the realy should be 110 volt with two contacts to hook up. When 110 is hooked up the relay closes and turns on the motor. Usually one leg is in series through the pressure and overheat switches and then to one of the 110 wires, which is generally the ground wire. The other contact goes to a shutoff switch (manual) and then to L1 or L2 to obtain 110 volts.

In the three wire single phase system two power wires (L1 and L2) together create 220 volts. Either of these in combination with the common or ground wire will create 110 volts. So when you run the 220 volt lines to the compressor you have 220 and two sources for 110. Use either of them for the 110, but not both or you will have 220 instead.

This is probably clear as mud, but the best I can discribe it. Make sure the voltages that the motor starter or relay is using for the coil that energizes it.

To add to that, depending on the equipment and the location in the country it is either 110 or 120 and 220 or 240, all the same thing. In New York the power company called it 117. Here it is 120, but does not matter. My power is actually 121 on one leg and 119 on the other.
Old 10-12-2004, 09:49 PM
  #6  
Registered User
 
Nevada's Avatar
 
Join Date: Oct 2002
Location: Logan, Utah
Posts: 638
Likes: 0
Received 0 Likes on 0 Posts
I need some cylinders aired up. Let us know when you are in business.

Will you be set up for Nirtrox?

Old 10-13-2004, 01:18 PM
  #7  
Registered User
Thread Starter
 
sdscuba's Avatar
 
Join Date: Aug 2002
Location: San Diego, CA
Posts: 81
Likes: 0
Received 2 Likes on 1 Post
It will be a full tech gas station in my garage, Nitrox, Trimix, and Argon.

I'm working on the storage cylinders and all of the blending. Dealing with 3500psi is an pain for finding inexpensive fittings.
Related Topics
Thread
Thread Starter
Forum
Replies
Last Post
firstgenW250
1st Gen. Ram - All Topics
5
06-17-2013 10:05 PM
Bo-man
3rd Gen High Performance and Accessories (5.9L Only)
8
09-25-2009 09:01 AM
TravisDj
12 Valve Engine and Drivetrain
2
12-16-2007 06:23 PM
sjester
12 Valve Engine and Drivetrain
1
08-19-2007 04:46 PM
Duallydog
3rd Gen Engine and Drivetrain -> 2003-2007
12
02-09-2006 09:00 AM



Quick Reply: Assistance wiring a compressor, please



All times are GMT -5. The time now is 11:05 AM.